24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

Testing & Commissioning interview questions

30 real Testing & Commissioning questions from the Plant & Utility Ops bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Insulation resistance test?

Junior
  1. A.DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
  2. B.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  3. C.ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  4. D.applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
Reveal the answer + AI explanation — free account

2. Which term means: "DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature"?

Junior
  1. A.Polarisation index
  2. B.Secondary injection
  3. C.Turns ratio test
  4. D.Insulation resistance test
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Insulation resistance test — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  2. B.Insulation resistance test — test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  3. C.Insulation resistance test — measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
  4. D.Insulation resistance test — DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
Reveal the answer + AI explanation — free account

4. What is Polarisation index?

Junior
  1. A.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  3. C.ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  4. D.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
Reveal the answer + AI explanation — free account

5. Which term means: "ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise"?

Junior
  1. A.Tan delta test
  2. B.Insulation resistance test
  3. C.Secondary injection
  4. D.Polarisation index
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Polarisation index — ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  2. B.Polarisation index — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  3. C.Polarisation index — DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  4. D.Polarisation index — test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
Reveal the answer + AI explanation — free account

7. What is Tan delta test?

Mid
  1. A.measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
  2. B.ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  3. C.DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  4. D.0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE
Reveal the answer + AI explanation — free account

8. Which term means: "measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge"?

Mid
  1. A.VLF hipot on XLPE cables
  2. B.Tan delta test
  3. C.Insulation resistance test
  4. D.CT polarity flick test
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Mid
  1. A.Tan delta test — test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.Tan delta test — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
  3. C.Tan delta test — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  4. D.Tan delta test — measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
Reveal the answer + AI explanation — free account

10. What is VLF hipot on XLPE cables?

Mid
  1. A.applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
  2. B.0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE
  3. C.ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  4. D.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
Reveal the answer + AI explanation — free account

11. Which term means: "0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE"?

Mid
  1. A.Tan delta test
  2. B.Turns ratio test
  3. C.VLF hipot on XLPE cables
  4. D.Winding resistance test
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Mid
  1. A.VLF hipot on XLPE cables — 0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE
  2. B.VLF hipot on XLPE cables — DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
  3. C.VLF hipot on XLPE cables — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  4. D.VLF hipot on XLPE cables — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
Reveal the answer + AI explanation — free account

13. What is Winding resistance test?

Junior
  1. A.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  3. C.DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  4. D.DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
Reveal the answer + AI explanation — free account

14. Which term means: "DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts"?

Junior
  1. A.Turns ratio test
  2. B.CT polarity flick test
  3. C.Pre-commissioning checklist
  4. D.Winding resistance test
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Junior
  1. A.Winding resistance test — applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
  2. B.Winding resistance test — DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  3. C.Winding resistance test — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  4. D.Winding resistance test — measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
Reveal the answer + AI explanation — free account

16. What is Turns ratio test?

Junior
  1. A.battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
  2. B.applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
  3. C.DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
  4. D.ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
Reveal the answer + AI explanation — free account

17. Which term means: "applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group"?

Junior
  1. A.Pre-commissioning checklist
  2. B.Winding resistance test
  3. C.Turns ratio test
  4. D.Secondary injection
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Junior
  1. A.Turns ratio test — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
  2. B.Turns ratio test — applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
  3. C.Turns ratio test — test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  4. D.Turns ratio test — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
Reveal the answer + AI explanation — free account

19. What is Secondary injection?

Mid
  1. A.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  3. C.ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
  4. D.0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE
Reveal the answer + AI explanation — free account

20. Which term means: "test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring"?

Mid
  1. A.VLF hipot on XLPE cables
  2. B.Polarisation index
  3. C.Insulation resistance test
  4. D.Secondary injection
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.Secondary injection — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
  2. B.Secondary injection — test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  3. C.Secondary injection — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  4. D.Secondary injection — ratio of the 10-minute to the 1-minute megger reading; IEEE 43 treats 2.0 or more as acceptable for class B and F insulation and below 1.0 as unsafe to energise
Reveal the answer + AI explanation — free account

22. What is Primary injection?

Mid
  1. A.DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  2. B.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  3. C.DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
  4. D.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
Reveal the answer + AI explanation — free account

23. Which term means: "high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end"?

Mid
  1. A.Primary injection
  2. B.Winding resistance test
  3. C.VLF hipot on XLPE cables
  4. D.Secondary injection
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Mid
  1. A.Primary injection — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  2. B.Primary injection — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  3. C.Primary injection — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
  4. D.Primary injection — measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
Reveal the answer + AI explanation — free account

25. What is CT polarity flick test?

Mid
  1. A.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  3. C.DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  4. D.battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
Reveal the answer + AI explanation — free account

26. Which term means: "battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond"?

Mid
  1. A.Winding resistance test
  2. B.Polarisation index
  3. C.CT polarity flick test
  4. D.VLF hipot on XLPE cables
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Mid
  1. A.CT polarity flick test — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  2. B.CT polarity flick test — applies voltage to the HV side and reads the LV at each tap to confirm the ratio within ±0.5% of nameplate per IEC 60076-1 and to verify the vector group
  3. C.CT polarity flick test — measures the dissipation factor of winding, bushing or cable insulation at several voltage steps; a value that rises with voltage (tip-up) points to moisture, voids or partial discharge
  4. D.CT polarity flick test — battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
Reveal the answer + AI explanation — free account

28. What is Pre-commissioning checklist?

Senior
  1. A.test kit feeds currents and voltages directly into the relay terminals to prove pick-up, timing and characteristic, without exercising the CTs, PTs or field wiring
  2. B.0.1 Hz withstand at about 2–3 Uo for 15–60 minutes per IEEE 400.2, preferred over DC hipot because DC leaves trapped space charge that damages XLPE
  3. C.ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
  4. D.battery touched across P1–P2 with positive on P1 gives a positive kick on an analogue meter whose positive lead is on S1, confirming that P1 and S1 correspond
Reveal the answer + AI explanation — free account

29. Which term means: "ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak"?

Senior
  1. A.Pre-commissioning checklist
  2. B.Polarisation index
  3. C.Turns ratio test
  4. D.CT polarity flick test
Reveal the answer + AI explanation — free account

30. Which statement is correct?

Senior
  1. A.Pre-commissioning checklist — high current from a loading transformer is passed through the primary conductor so CT ratio, polarity, secondary wiring and relay response are proved end to end
  2. B.Pre-commissioning checklist — DC resistance of every winding at every tap, compared phase to phase and with factory values within about 2%, to catch loose leads, broken strands or poor OLTC contacts
  3. C.Pre-commissioning checklist — DC megger test at 500 V to 5 kV between winding and earth, with a rule-of-thumb minimum of 1 MΩ per kV of rating plus 1 MΩ, corrected to a reference temperature
  4. D.Pre-commissioning checklist — ordered proof before first charging: mechanical completion, IR and continuity, relay settings from the approved sheet, trip and interlock checks, then charging and a no-load soak
Reveal the answer + AI explanation — free account

Free to start

Answers, AI explanations, and a free readiness check

Sign up free to check your answers with explanations, ask the AI tutor anything on any question, and take the free 2-minute readiness check for a scored result. The full AI mock interview, scored like a real panel, unlocks with Pro.

Practice Testing & Commissioning free