24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

Grid & Utility Operations interview questions

30 real Grid & Utility Operations questions from the Plant & Utility Ops bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Load despatch hierarchy?

Junior
  1. A.IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  2. B.three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  3. C.CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  4. D.NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
Reveal the answer + AI explanation — free account

2. Which term means: "NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state"?

Junior
  1. A.Islanding scheme
  2. B.Energy management system
  3. C.Black start
  4. D.Load despatch hierarchy
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Load despatch hierarchy — CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  2. B.Load despatch hierarchy — NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
  3. C.Load despatch hierarchy — aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  4. D.Load despatch hierarchy — restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures
Reveal the answer + AI explanation — free account

4. What is Indian Electricity Grid Code?

Junior
  1. A.df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  2. B.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  3. C.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  4. D.CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
Reveal the answer + AI explanation — free account

5. Which term means: "CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users"?

Junior
  1. A.Indian Electricity Grid Code
  2. B.Availability-based tariff
  3. C.Islanding scheme
  4. D.Load despatch hierarchy
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Indian Electricity Grid Code — CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  2. B.Indian Electricity Grid Code — NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
  3. C.Indian Electricity Grid Code — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
  4. D.Indian Electricity Grid Code — IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
Reveal the answer + AI explanation — free account

7. What is Grid frequency band?

Junior
  1. A.IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  2. B.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  3. C.CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
  4. D.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
Reveal the answer + AI explanation — free account

8. Which term means: "IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band"?

Junior
  1. A.Load despatch hierarchy
  2. B.Grid frequency band
  3. C.Black start
  4. D.Deviation settlement mechanism
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.Grid frequency band — aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  2. B.Grid frequency band — IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  3. C.Grid frequency band — three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  4. D.Grid frequency band — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
Reveal the answer + AI explanation — free account

10. What is Availability-based tariff?

Mid
  1. A.CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  2. B.three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  3. C.about 3–4% of energy wheeled on the ISTS, computed weekly by the RLDC from metered injections and drawals and apportioned to all users of the region pro rata
  4. D.IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
Reveal the answer + AI explanation — free account

11. Which term means: "three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule"?

Mid
  1. A.Deviation settlement mechanism
  2. B.Availability-based tariff
  3. C.Islanding scheme
  4. D.Load despatch hierarchy
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Mid
  1. A.Availability-based tariff — aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  2. B.Availability-based tariff — IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  3. C.Availability-based tariff — df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  4. D.Availability-based tariff — three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
Reveal the answer + AI explanation — free account

13. What is Deviation settlement mechanism?

Senior
  1. A.CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  2. B.IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  3. C.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  4. D.CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
Reveal the answer + AI explanation — free account

14. Which term means: "CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange"?

Senior
  1. A.Availability-based tariff
  2. B.AT&C losses
  3. C.Inter-state transmission losses
  4. D.Deviation settlement mechanism
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Senior
  1. A.Deviation settlement mechanism — df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  2. B.Deviation settlement mechanism — control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  3. C.Deviation settlement mechanism — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
  4. D.Deviation settlement mechanism — NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
Reveal the answer + AI explanation — free account

16. What is Energy management system?

Mid
  1. A.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  2. B.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  3. C.NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
  4. D.restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures
Reveal the answer + AI explanation — free account

17. Which term means: "control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP"?

Mid
  1. A.Inter-state transmission losses
  2. B.Energy management system
  3. C.Grid frequency band
  4. D.Indian Electricity Grid Code
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.Energy management system — control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  2. B.Energy management system — about 3–4% of energy wheeled on the ISTS, computed weekly by the RLDC from metered injections and drawals and apportioned to all users of the region pro rata
  3. C.Energy management system — IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
  4. D.Energy management system — CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
Reveal the answer + AI explanation — free account

19. What is Islanding scheme?

Mid
  1. A.df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  2. B.three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  3. C.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  4. D.IEGC requires system frequency to be held between 49.90 and 50.05 Hz, with generators giving primary response outside a ±0.03 Hz dead band
Reveal the answer + AI explanation — free account

20. Which term means: "df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances"?

Mid
  1. A.Grid frequency band
  2. B.Energy management system
  3. C.Islanding scheme
  4. D.AT&C losses
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.Islanding scheme — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
  2. B.Islanding scheme — restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures
  3. C.Islanding scheme — df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  4. D.Islanding scheme — aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
Reveal the answer + AI explanation — free account

22. What is Black start?

Senior
  1. A.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  2. B.three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  3. C.restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures
  4. D.df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
Reveal the answer + AI explanation — free account

23. Which term means: "restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures"?

Senior
  1. A.Inter-state transmission losses
  2. B.Deviation settlement mechanism
  3. C.Black start
  4. D.Energy management system
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Senior
  1. A.Black start — df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  2. B.Black start — control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  3. C.Black start — restoration after total collapse using hydro or gas units that can start without grid supply to energise dead lines and give station supply to thermal units, per RLDC procedures
  4. D.Black start — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
Reveal the answer + AI explanation — free account

25. What is Inter-state transmission losses?

Mid
  1. A.control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  2. B.about 3–4% of energy wheeled on the ISTS, computed weekly by the RLDC from metered injections and drawals and apportioned to all users of the region pro rata
  3. C.NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
  4. D.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
Reveal the answer + AI explanation — free account

26. Which term means: "about 3–4% of energy wheeled on the ISTS, computed weekly by the RLDC from metered injections and drawals and apportioned to all users of the region pro rata"?

Mid
  1. A.Load despatch hierarchy
  2. B.Availability-based tariff
  3. C.AT&C losses
  4. D.Inter-state transmission losses
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Mid
  1. A.Inter-state transmission losses — control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  2. B.Inter-state transmission losses — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
  3. C.Inter-state transmission losses — NLDC under Grid Controller of India (formerly POSOCO) at the top, five RLDCs for the NR, WR, SR, ER and NER regions, and an SLDC in each state
  4. D.Inter-state transmission losses — about 3–4% of energy wheeled on the ISTS, computed weekly by the RLDC from metered injections and drawals and apportioned to all users of the region pro rata
Reveal the answer + AI explanation — free account

28. What is AT&C losses?

Junior
  1. A.CERC regulation, 2023 edition in force from October 2023, setting connectivity, planning, operation, scheduling and protection obligations for all grid users
  2. B.three-part tariff: capacity charge paid on declared availability, energy charge on scheduled energy, and a deviation charge for departing from the schedule
  3. C.df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  4. D.aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
Reveal the answer + AI explanation — free account

29. Which term means: "aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23"?

Junior
  1. A.Indian Electricity Grid Code
  2. B.Islanding scheme
  3. C.Grid frequency band
  4. D.AT&C losses
Reveal the answer + AI explanation — free account

30. Which statement is correct?

Junior
  1. A.AT&C losses — df/dt and under-frequency relays separate a generating station with a matched load pocket from a collapsing grid, as Mumbai's scheme has done during regional disturbances
  2. B.AT&C losses — control-centre software above SCADA that runs state estimation, contingency analysis and automatic generation control on telemetry received over IEC 60870-5-104 and ICCP
  3. C.AT&C losses — aggregate technical and commercial loss equals one minus billing efficiency times collection efficiency; India's figure fell from about 22% in FY21 to about 15% by FY23
  4. D.AT&C losses — CERC DSM Regulations 2022 charge each 15-minute block of deviation from schedule at a normal rate with frequency- and volume-linked multipliers, replacing unscheduled interchange
Reveal the answer + AI explanation — free account

Free to start

Answers, AI explanations, and a free readiness check

Sign up free to check your answers with explanations, ask the AI tutor anything on any question, and take the free 2-minute readiness check for a scored result. The full AI mock interview, scored like a real panel, unlocks with Pro.

Practice Grid & Utility Operations free