24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

HVAC & Plant Utilities interview questions

27 real HVAC & Plant Utilities questions from the Production & Plant bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Chiller specific power?

Junior
  1. A.kW per ton of refrigeration, about 0.6 for a centrifugal and 0.8–1.0 for a screw chiller, the key efficiency figure of a plant
  2. B.1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  3. C.fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  4. D.kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
Reveal the answer + AI explanation — free account

2. Which term means: "kW per ton of refrigeration, about 0.6 for a centrifugal and 0.8–1.0 for a screw chiller, the key efficiency figure of a plant"?

Junior
  1. A.Steam trap
  2. B.Chiller specific power
  3. C.Cooling tower approach
  4. D.Cycles of concentration
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Chiller specific power — kW per ton of refrigeration, about 0.6 for a centrifugal and 0.8–1.0 for a screw chiller, the key efficiency figure of a plant
  2. B.Chiller specific power — difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  3. C.Chiller specific power — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  4. D.Chiller specific power — 1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
Reveal the answer + AI explanation — free account

4. What is Cooling tower approach?

Junior
  1. A.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  2. B.valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
  3. C.ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  4. D.difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
Reveal the answer + AI explanation — free account

5. Which term means: "difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop"?

Junior
  1. A.Chiller specific power
  2. B.Steam trap
  3. C.Cooling tower approach
  4. D.Cycles of concentration
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Cooling tower approach — 1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  2. B.Cooling tower approach — direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  3. C.Cooling tower approach — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  4. D.Cooling tower approach — difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
Reveal the answer + AI explanation — free account

7. What is Indian Boiler Regulations?

Junior
  1. A.ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  2. B.kW per ton of refrigeration, about 0.6 for a centrifugal and 0.8–1.0 for a screw chiller, the key efficiency figure of a plant
  3. C.fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  4. D.1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
Reveal the answer + AI explanation — free account

8. Which term means: "1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity"?

Junior
  1. A.Indian Boiler Regulations
  2. B.Variable frequency drive savings
  3. C.Compressed air specific power
  4. D.Energy audit
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.Indian Boiler Regulations — fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  2. B.Indian Boiler Regulations — kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
  3. C.Indian Boiler Regulations — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  4. D.Indian Boiler Regulations — 1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
Reveal the answer + AI explanation — free account

10. What is Boiler efficiency methods?

Mid
  1. A.ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  2. B.fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  3. C.kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
  4. D.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
Reveal the answer + AI explanation — free account

11. Which term means: "direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses"?

Mid
  1. A.Cooling tower approach
  2. B.Cycles of concentration
  3. C.Indian Boiler Regulations
  4. D.Boiler efficiency methods
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Mid
  1. A.Boiler efficiency methods — ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  2. B.Boiler efficiency methods — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  3. C.Boiler efficiency methods — 1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  4. D.Boiler efficiency methods — direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
Reveal the answer + AI explanation — free account

13. What is Compressed air specific power?

Mid
  1. A.preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  2. B.difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  3. C.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  4. D.kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
Reveal the answer + AI explanation — free account

14. Which term means: "kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation"?

Mid
  1. A.Chiller specific power
  2. B.Cooling tower approach
  3. C.Indian Boiler Regulations
  4. D.Compressed air specific power
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Mid
  1. A.Compressed air specific power — kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
  2. B.Compressed air specific power — ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  3. C.Compressed air specific power — difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  4. D.Compressed air specific power — fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
Reveal the answer + AI explanation — free account

16. What is Cycles of concentration?

Mid
  1. A.1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  2. B.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  3. C.ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  4. D.difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
Reveal the answer + AI explanation — free account

17. Which term means: "ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling"?

Mid
  1. A.Indian Boiler Regulations
  2. B.Cooling tower approach
  3. C.Chiller specific power
  4. D.Cycles of concentration
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.Cycles of concentration — valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
  2. B.Cycles of concentration — kW per ton of refrigeration, about 0.6 for a centrifugal and 0.8–1.0 for a screw chiller, the key efficiency figure of a plant
  3. C.Cycles of concentration — ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  4. D.Cycles of concentration — direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
Reveal the answer + AI explanation — free account

19. What is Energy audit?

Mid
  1. A.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  2. B.difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  3. C.ratio of dissolved solids in cooling water to that in make-up water, run at 3–5 to save water without scaling
  4. D.preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
Reveal the answer + AI explanation — free account

20. Which term means: "preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers"?

Mid
  1. A.Cooling tower approach
  2. B.Indian Boiler Regulations
  3. C.Compressed air specific power
  4. D.Energy audit
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.Energy audit — direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  2. B.Energy audit — fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  3. C.Energy audit — valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
  4. D.Energy audit — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
Reveal the answer + AI explanation — free account

22. What is Variable frequency drive savings?

Senior
  1. A.1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  2. B.fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  3. C.preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  4. D.kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
Reveal the answer + AI explanation — free account

23. Which term means: "fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half"?

Senior
  1. A.Cycles of concentration
  2. B.Boiler efficiency methods
  3. C.Indian Boiler Regulations
  4. D.Variable frequency drive savings
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Senior
  1. A.Variable frequency drive savings — kW per 100 cfm delivered, around 18–20 for a good screw compressor, with leaks often wasting 20–30% of generation
  2. B.Variable frequency drive savings — fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  3. C.Variable frequency drive savings — 1950 rules under the Boilers Act 1923 requiring approved design, certified welders and annual inspection for any boiler above 22.75 litres capacity
  4. D.Variable frequency drive savings — valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
Reveal the answer + AI explanation — free account

25. What is Steam trap?

Senior
  1. A.valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
  2. B.difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  3. C.direct method compares steam output with fuel input, while the indirect method of IS 8753 sums stack, radiation and unburnt losses
  4. D.fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
Reveal the answer + AI explanation — free account

26. Which term means: "valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss"?

Senior
  1. A.Boiler efficiency methods
  2. B.Steam trap
  3. C.Compressed air specific power
  4. D.Cooling tower approach
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Senior
  1. A.Steam trap — preliminary walk-through or detailed instrumented study under the Energy Conservation Act 2001, mandatory for designated consumers
  2. B.Steam trap — difference between outlet cold-water temperature and ambient wet-bulb, typically 3–5 °C, while range is the inlet-to-outlet water drop
  3. C.Steam trap — fan and pump power falls with the cube of speed under the affinity laws, so a 20% speed reduction cuts power by about half
  4. D.Steam trap — valve that discharges condensate while holding steam, in thermodynamic, float or thermostatic types, with failed-open traps a major steam loss
Reveal the answer + AI explanation — free account