24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

Substation Design interview questions

33 real Substation Design questions from the Electrical Design bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Single line diagram?

Junior
  1. A.one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
  2. B.gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
  3. C.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  4. D.an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
Reveal the answer + AI explanation — free account

2. Which term means: "one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation"?

Junior
  1. A.Main and transfer bus
  2. B.Single line diagram
  3. C.Bay
  4. D.Switchyard shielding
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Single line diagram — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.Single line diagram — minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  3. C.Single line diagram — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.Single line diagram — one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
Reveal the answer + AI explanation — free account

4. What is Main and transfer bus?

Junior
  1. A.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
  3. C.minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  4. D.transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
Reveal the answer + AI explanation — free account

5. Which term means: "transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV"?

Junior
  1. A.Main and transfer bus
  2. B.GIS vs AIS
  3. C.Double bus single breaker
  4. D.Isolator vs breaker
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Main and transfer bus — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.Main and transfer bus — transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
  3. C.Main and transfer bus — each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
  4. D.Main and transfer bus — three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
Reveal the answer + AI explanation — free account

7. What is Bay?

Junior
  1. A.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
  3. C.an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
Reveal the answer + AI explanation — free account

8. Which term means: "the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout"?

Junior
  1. A.Isolator vs breaker
  2. B.Main and transfer bus
  3. C.Bay
  4. D.One-and-a-half breaker scheme
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.Bay — transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
  2. B.Bay — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  3. C.Bay — minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  4. D.Bay — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
Reveal the answer + AI explanation — free account

10. What is Isolator vs breaker?

Junior
  1. A.overhead earth wires or masts placed so the rolling-sphere or 30–45° protective-angle zone covers every live conductor per IS/IEC 62305
  2. B.an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  3. C.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  4. D.three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
Reveal the answer + AI explanation — free account

11. Which term means: "an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks"?

Junior
  1. A.Isolator vs breaker
  2. B.GIS vs AIS
  3. C.Switchyard shielding
  4. D.Main and transfer bus
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Junior
  1. A.Isolator vs breaker — three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
  2. B.Isolator vs breaker — selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  3. C.Isolator vs breaker — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  4. D.Isolator vs breaker — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
Reveal the answer + AI explanation — free account

13. What is One-and-a-half breaker scheme?

Mid
  1. A.transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
  2. B.each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
  3. C.three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
  4. D.grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
Reveal the answer + AI explanation — free account

14. Which term means: "three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above"?

Mid
  1. A.Phase-to-earth clearance
  2. B.Isolator vs breaker
  3. C.Main and transfer bus
  4. D.One-and-a-half breaker scheme
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Mid
  1. A.One-and-a-half breaker scheme — grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
  2. B.One-and-a-half breaker scheme — gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
  3. C.One-and-a-half breaker scheme — three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
  4. D.One-and-a-half breaker scheme — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
Reveal the answer + AI explanation — free account

16. What is Double bus single breaker?

Mid
  1. A.one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
  2. B.overhead earth wires or masts placed so the rolling-sphere or 30–45° protective-angle zone covers every live conductor per IS/IEC 62305
  3. C.gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
  4. D.each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
Reveal the answer + AI explanation — free account

17. Which term means: "each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one"?

Mid
  1. A.Double bus single breaker
  2. B.GIS vs AIS
  3. C.Phase-to-earth clearance
  4. D.Main and transfer bus
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.Double bus single breaker — each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
  2. B.Double bus single breaker — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  3. C.Double bus single breaker — minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  4. D.Double bus single breaker — transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
Reveal the answer + AI explanation — free account

19. What is Phase-to-earth clearance?

Mid
  1. A.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  3. C.an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
Reveal the answer + AI explanation — free account

20. Which term means: "minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV"?

Mid
  1. A.Switchyard shielding
  2. B.Main and transfer bus
  3. C.GIS vs AIS
  4. D.Phase-to-earth clearance
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.Phase-to-earth clearance — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  2. B.Phase-to-earth clearance — selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  3. C.Phase-to-earth clearance — grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
  4. D.Phase-to-earth clearance — minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
Reveal the answer + AI explanation — free account

22. What is IEEE 80 earthing mat design?

Mid
  1. A.grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
  2. B.transfer bus with a bus coupler lets a feeder breaker be taken out for maintenance while the feeder stays supplied, common at 132 kV
  3. C.one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
  4. D.selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
Reveal the answer + AI explanation — free account

23. Which term means: "grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity"?

Mid
  1. A.Main and transfer bus
  2. B.Single line diagram
  3. C.IEEE 80 earthing mat design
  4. D.Bay
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Mid
  1. A.IEEE 80 earthing mat design — grid conductor sized on fault current and duration, then mesh and step voltages are checked against tolerable limits from body weight and gravel resistivity
  2. B.IEEE 80 earthing mat design — selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  3. C.IEEE 80 earthing mat design — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.IEEE 80 earthing mat design — one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
Reveal the answer + AI explanation — free account

25. What is GIS vs AIS?

Mid
  1. A.gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
  2. B.each feeder can be transferred between two main buses by isolators, allowing bus maintenance without feeder outage but breaker maintenance needs one
  3. C.the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  4. D.overhead earth wires or masts placed so the rolling-sphere or 30–45° protective-angle zone covers every live conductor per IS/IEC 62305
Reveal the answer + AI explanation — free account

26. Which term means: "gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties"?

Mid
  1. A.Phase-to-earth clearance
  2. B.GIS vs AIS
  3. C.One-and-a-half breaker scheme
  4. D.Insulation coordination
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Mid
  1. A.GIS vs AIS — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
  2. B.GIS vs AIS — minimum air distance from live parts to earthed structures, about 1300 mm at 132 kV, 2100 mm at 220 kV and 3500 mm at 400 kV
  3. C.GIS vs AIS — selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  4. D.GIS vs AIS — gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
Reveal the answer + AI explanation — free account

28. What is Insulation coordination?

Senior
  1. A.selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  2. B.gas-insulated switchgear needs about 10–20% of the air-insulated footprint and suits polluted or urban sites, at higher capital cost and SF6 handling duties
  3. C.an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.one-line representation of the three-phase system showing transformers, breakers, isolators, CTs, PTs and protection, the master drawing of any substation
Reveal the answer + AI explanation — free account

29. Which term means: "selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071"?

Senior
  1. A.Single line diagram
  2. B.GIS vs AIS
  3. C.Double bus single breaker
  4. D.Insulation coordination
Reveal the answer + AI explanation — free account

30. Which statement is correct?

Senior
  1. A.Insulation coordination — three breakers per two circuits between two main buses, giving no feeder outage for any breaker fault, standard at 400 kV and above
  2. B.Insulation coordination — selecting equipment withstand levels (BIL/SIL) against surge arrester protective levels with a margin of at least 20% per IEC 60071
  3. C.Insulation coordination — an isolator is an off-load device giving visible isolation and must be operated only after the breaker has opened, enforced by interlocks
  4. D.Insulation coordination — the set of breaker, isolators, CTs, PT and earth switch controlling one circuit, whose width and depth fix the switchyard layout
Reveal the answer + AI explanation — free account

Showing 30 of 33 Substation Design questions — the full set, with answers, explanations and an AI tutor on every question, is inside.