24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

Electrical Standards & Regulations interview questions

30 real Electrical Standards & Regulations questions from the Electrical Design bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is IEC 60364?

Junior
  1. A.US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  2. B.international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  3. C.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  4. D.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
Reveal the answer + AI explanation — free account

2. Which term means: "international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment"?

Junior
  1. A.Electricity Act 2003
  2. B.IEC 60947
  3. C.Voltage classification
  4. D.IEC 60364
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.IEC 60364 — US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  2. B.IEC 60364 — international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  3. C.IEC 60364 — Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations
  4. D.IEC 60364 — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
Reveal the answer + AI explanation — free account

4. What is IS 732?

Junior
  1. A.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  2. B.Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations
  3. C.CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  4. D.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
Reveal the answer + AI explanation — free account

5. Which term means: "Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations"?

Junior
  1. A.Voltage classification
  2. B.NEC continuous-load rule
  3. C.Hazardous area zones
  4. D.IS 732
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.IS 732 — energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  2. B.IS 732 — Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations
  3. C.IS 732 — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  4. D.IS 732 — international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
Reveal the answer + AI explanation — free account

7. What is CEA Safety Regulations 2023?

Junior
  1. A.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  2. B.Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  3. C.CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
  4. D.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
Reveal the answer + AI explanation — free account

8. Which term means: "Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956"?

Junior
  1. A.Voltage classification
  2. B.Electricity Act 2003
  3. C.CEA Safety Regulations 2023
  4. D.NEC continuous-load rule
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.CEA Safety Regulations 2023 — LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  2. B.CEA Safety Regulations 2023 — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  3. C.CEA Safety Regulations 2023 — IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  4. D.CEA Safety Regulations 2023 — CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
Reveal the answer + AI explanation — free account

10. What is Electricity Act 2003?

Junior
  1. A.Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  2. B.CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  3. C.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  4. D.Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations
Reveal the answer + AI explanation — free account

11. Which term means: "central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role"?

Junior
  1. A.IEC 60947
  2. B.Electricity Act 2003
  3. C.CEA Safety Regulations 2023
  4. D.Hazardous area zones
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Junior
  1. A.Electricity Act 2003 — US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  2. B.Electricity Act 2003 — CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
  3. C.Electricity Act 2003 — international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  4. D.Electricity Act 2003 — central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
Reveal the answer + AI explanation — free account

13. What is Voltage classification?

Mid
  1. A.CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  2. B.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  3. C.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  4. D.international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
Reveal the answer + AI explanation — free account

14. Which term means: "CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV"?

Mid
  1. A.IEC 60947
  2. B.IS 732
  3. C.Voltage classification
  4. D.Electrical Inspector approval
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Mid
  1. A.Voltage classification — CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  2. B.Voltage classification — US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  3. C.Voltage classification — central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  4. D.Voltage classification — CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
Reveal the answer + AI explanation — free account

16. What is IEC 60947?

Mid
  1. A.LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  2. B.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  3. C.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  4. D.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
Reveal the answer + AI explanation — free account

17. Which term means: "LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)"?

Mid
  1. A.Voltage classification
  2. B.CEA Safety Regulations 2023
  3. C.IEC 60947
  4. D.Hazardous area zones
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.IEC 60947 — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  2. B.IEC 60947 — international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  3. C.IEC 60947 — US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  4. D.IEC 60947 — LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
Reveal the answer + AI explanation — free account

19. What is ISO 50001?

Mid
  1. A.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  2. B.US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  3. C.international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  4. D.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
Reveal the answer + AI explanation — free account

20. Which term means: "energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses"?

Mid
  1. A.IS 732
  2. B.ISO 50001
  3. C.CEA Safety Regulations 2023
  4. D.NEC continuous-load rule
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.ISO 50001 — CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  2. B.ISO 50001 — LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  3. C.ISO 50001 — energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  4. D.ISO 50001 — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
Reveal the answer + AI explanation — free account

22. What is NEC continuous-load rule?

Mid
  1. A.LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  2. B.international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
  3. C.central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  4. D.US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
Reveal the answer + AI explanation — free account

23. Which term means: "US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients"?

Mid
  1. A.IEC 60947
  2. B.ISO 50001
  3. C.NEC continuous-load rule
  4. D.IS 732
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Mid
  1. A.NEC continuous-load rule — Indian code of practice for electrical wiring installations, aligned to IEC 60364, covering design, selection and verification of LV installations
  2. B.NEC continuous-load rule — LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  3. C.NEC continuous-load rule — central act that created CEA, CERC and SERCs, introduced open access and licensing and gives Electrical Inspectors their statutory role
  4. D.NEC continuous-load rule — US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
Reveal the answer + AI explanation — free account

25. What is Hazardous area zones?

Senior
  1. A.US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  2. B.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  3. C.LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  4. D.international standard for low-voltage electrical installations covering protection against shock, thermal effects, overcurrent and selection of equipment
Reveal the answer + AI explanation — free account

26. Which term means: "IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment"?

Senior
  1. A.Hazardous area zones
  2. B.CEA Safety Regulations 2023
  3. C.NEC continuous-load rule
  4. D.Electricity Act 2003
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Senior
  1. A.Hazardous area zones — energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  2. B.Hazardous area zones — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  3. C.Hazardous area zones — CEA regulations define low voltage up to 250 V, medium up to 650 V, high up to 33 kV and extra-high above 33 kV
  4. D.Hazardous area zones — IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
Reveal the answer + AI explanation — free account

28. What is Electrical Inspector approval?

Senior
  1. A.IS 5572 / IEC 60079-10 classify Zone 0 continuous, Zone 1 likely in normal operation and Zone 2 unlikely and brief, dictating Ex d or Ex e equipment
  2. B.energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
  3. C.US installation code (NFPA 70) sizes breakers and conductors at 125% of a load that runs three hours or more, met on projects with American clients
  4. D.CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
Reveal the answer + AI explanation — free account

29. Which term means: "CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years"?

Senior
  1. A.IS 732
  2. B.Electricity Act 2003
  3. C.Electrical Inspector approval
  4. D.Voltage classification
Reveal the answer + AI explanation — free account

30. Which statement is correct?

Senior
  1. A.Electrical Inspector approval — Central Electricity Authority (Measures relating to Safety and Electric Supply) Regulations that replaced the 2010 regulations, themselves successors of the IE Rules 1956
  2. B.Electrical Inspector approval — CEA regulations require HV/EHV installations to be inspected and approved before energisation and periodically tested, typically every five years
  3. C.Electrical Inspector approval — LV switchgear and controlgear standard; Part 2 for circuit breakers (Icu, Ics) and Part 4-1 for contactors and starters (AC-3 category)
  4. D.Electrical Inspector approval — energy management system standard using Plan-Do-Check-Act with an energy baseline, energy performance indicators and significant energy uses
Reveal the answer + AI explanation — free account

Free to start

Answers, AI explanations, and a free readiness check

Sign up free to check your answers with explanations, ask the AI tutor anything on any question, and take the free 2-minute readiness check for a scored result. The full AI mock interview, scored like a real panel, unlocks with Pro.