24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

RCC Design (IS 456) interview questions

27 real RCC Design (IS 456) questions from the Civil Design & Codes bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Partial safety factors for materials?

Junior
  1. A.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  2. B.nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  3. C.Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  4. D.As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
Reveal the answer + AI explanation — free account

2. Which term means: "γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement"?

Junior
  1. A.Span-to-effective-depth control
  2. B.Partial safety factors for materials
  3. C.Development length
  4. D.Minimum eccentricity for columns
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Partial safety factors for materials — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  2. B.Partial safety factors for materials — Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  3. C.Partial safety factors for materials — nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  4. D.Partial safety factors for materials — γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
Reveal the answer + AI explanation — free account

4. What is Partial safety factors for loads?

Junior
  1. A.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  2. B.Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  3. C.Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  4. D.As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
Reveal the answer + AI explanation — free account

5. Which term means: "Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability"?

Junior
  1. A.Partial safety factors for loads
  2. B.Development length
  3. C.Partial safety factors for materials
  4. D.Span-to-effective-depth control
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Partial safety factors for loads — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  2. B.Partial safety factors for loads — As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
  3. C.Partial safety factors for loads — Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  4. D.Partial safety factors for loads — basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
Reveal the answer + AI explanation — free account

7. What is Nominal cover by exposure?

Junior
  1. A.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  2. B.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  3. C.every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  4. D.Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
Reveal the answer + AI explanation — free account

8. Which term means: "Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm"?

Junior
  1. A.Span-to-effective-depth control
  2. B.Partial safety factors for materials
  3. C.Crack width limit
  4. D.Nominal cover by exposure
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.Nominal cover by exposure — surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  2. B.Nominal cover by exposure — Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  3. C.Nominal cover by exposure — Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  4. D.Nominal cover by exposure — γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
Reveal the answer + AI explanation — free account

10. What is Minimum tension steel in beams?

Junior
  1. A.As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
  2. B.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  3. C.every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  4. D.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
Reveal the answer + AI explanation — free account

11. Which term means: "As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area"?

Junior
  1. A.Span-to-effective-depth control
  2. B.Minimum tension steel in beams
  3. C.Partial safety factors for loads
  4. D.Crack width limit
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Junior
  1. A.Minimum tension steel in beams — Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  2. B.Minimum tension steel in beams — As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
  3. C.Minimum tension steel in beams — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  4. D.Minimum tension steel in beams — Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
Reveal the answer + AI explanation — free account

13. What is Development length?

Junior
  1. A.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  2. B.Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  3. C.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  4. D.Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
Reveal the answer + AI explanation — free account

14. Which term means: "Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression"?

Junior
  1. A.Minimum eccentricity for columns
  2. B.Development length
  3. C.Partial safety factors for materials
  4. D.Minimum tension steel in beams
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Junior
  1. A.Development length — every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  2. B.Development length — nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  3. C.Development length — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  4. D.Development length — surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
Reveal the answer + AI explanation — free account

16. What is Span-to-effective-depth control?

Mid
  1. A.Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  2. B.every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  3. C.nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  4. D.basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
Reveal the answer + AI explanation — free account

17. Which term means: "basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages"?

Mid
  1. A.Span-to-effective-depth control
  2. B.Minimum eccentricity for columns
  3. C.Partial safety factors for loads
  4. D.Minimum tension steel in beams
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.Span-to-effective-depth control — Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  2. B.Span-to-effective-depth control — nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  3. C.Span-to-effective-depth control — Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  4. D.Span-to-effective-depth control — basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
Reveal the answer + AI explanation — free account

19. What is Shear design procedure?

Mid
  1. A.Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  2. B.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  3. C.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  4. D.nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
Reveal the answer + AI explanation — free account

20. Which term means: "nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess"?

Mid
  1. A.Minimum tension steel in beams
  2. B.Nominal cover by exposure
  3. C.Shear design procedure
  4. D.Development length
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.Shear design procedure — nominal shear Vu/bd is compared with τc from Table 19 for the steel percentage, must not exceed τc,max of Table 20, and stirrups carry the excess
  2. B.Shear design procedure — Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  3. C.Shear design procedure — every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  4. D.Shear design procedure — γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
Reveal the answer + AI explanation — free account

22. What is Crack width limit?

Senior
  1. A.As/bd must be at least 0.85/fy, about 0.20 percent for Fe415, and total steel on either face may not exceed 4 percent of gross area
  2. B.Table 18 uses 1.5 on dead plus live load, 1.2 when dead, live and wind or earthquake act together, and 0.9 on dead load when it helps stability
  3. C.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  4. D.surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
Reveal the answer + AI explanation — free account

23. Which term means: "surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F"?

Senior
  1. A.Development length
  2. B.Crack width limit
  3. C.Partial safety factors for materials
  4. D.Partial safety factors for loads
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Senior
  1. A.Crack width limit — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
  2. B.Crack width limit — γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  3. C.Crack width limit — surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  4. D.Crack width limit — basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
Reveal the answer + AI explanation — free account

25. What is Minimum eccentricity for columns?

Senior
  1. A.Table 16 requires 20 mm for mild, 30 mm moderate, 45 mm severe, 50 mm very severe and 75 mm extreme exposure, with footings never below 50 mm
  2. B.γm is 1.5 for concrete and 1.15 for steel, so design strengths become 0.446 fck in the stress block and 0.87 fy for reinforcement
  3. C.every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  4. D.basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
Reveal the answer + AI explanation — free account

26. Which term means: "every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately"?

Senior
  1. A.Crack width limit
  2. B.Partial safety factors for materials
  3. C.Minimum eccentricity for columns
  4. D.Partial safety factors for loads
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Senior
  1. A.Minimum eccentricity for columns — surface crack width is limited to 0.3 mm generally, 0.2 mm where aggressive exposure exists and 0.1 mm for very severe conditions, checked by Annex F
  2. B.Minimum eccentricity for columns — basic ratios of 7 for cantilevers, 20 for simply supported and 26 for continuous spans up to 10 m, modified for tension and compression steel percentages
  3. C.Minimum eccentricity for columns — every column is designed for at least L/500 plus D/30 or 20 mm eccentricity, whichever is more, about each axis separately
  4. D.Minimum eccentricity for columns — Ld = φ σs / (4 τbd), with design bond stress from Table for plain bars increased 60 percent for deformed bars and 25 percent more in compression
Reveal the answer + AI explanation — free account

Free to start

Answers, AI explanations, and a free readiness check

Sign up free to check your answers with explanations, ask the AI tutor anything on any question, and take the free 2-minute readiness check for a scored result. The full AI mock interview, scored like a real panel, unlocks with Pro.

Practice RCC Design (IS 456) free