24,000+ questions & coding problemsSoftware & IT16,274 questionsGovernment jobs26 examsAptitudenew questions every timeAI practice interviewwith feedback65 topics to practiseMechanical1,149 questionsGATE ME9 papersEngineering Mathematics381 questions2-minute checkfreeDSA Problems1,422Civil1,005 questionsGATE CE9 papersCS Fundamentals1,209 questionsYour scores6 skillsSystem Design25Electrical / EEE1,047 questionsGATE EE9 papersRun your codeC++ · Java · PythonLow-Level Design144Electronics & Comm.975 questionsGATE EC9 papersAI help on every questionFull-Stack6,282Chemical1,005 questionsGATE CH9 papersAI whiteboardsystem designWork abroadEurope · remote · transfersESE ME1 paperGATE practice papers2019–2026ESE CE1 paperDate alertsbefore the last dateESE EE1 paperBehavioural courseHR round practiceESE ET1 paperResume optimizerSSC JE ME1 paperApplication trackerSSC JE CE1 paperCompany-wise prepSSC JE EE1 paperRole roadmapsRRB JE1 subjectPriced in ₹UPI · cardsISRO SC1 paperGATE CS9 papersIBPS SO IT1 paperUGC NET CS1 paperSSC CGL26 papersIBPS PO26 papersRRB NTPC26 papersSSC CHSL26 papersIBPS Clerk26 papersSBI Clerk26 papersRRB Group D26 papersSSC CPO26 papersSSC GD26 papers

Process Instrumentation Basics interview questions

27 real Process Instrumentation Basics questions from the Chemical Core bank, as asked in Indian campus drives and tech interviews. Every question has a verified answer and an AI-tutor explanation on placd — free to start.

1. What is Orifice plate flow measurement?

Junior
  1. A.ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  2. B.differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  3. C.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  4. D.platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
Reveal the answer + AI explanation — free account

2. Which term means: "differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction"?

Junior
  1. A.Orifice plate flow measurement
  2. B.Coriolis mass flow meter
  3. C.Pt100 RTD
  4. D.Turndown ratio
Reveal the answer + AI explanation — free account

3. Which statement is correct?

Junior
  1. A.Orifice plate flow measurement — platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  2. B.Orifice plate flow measurement — hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
  3. C.Orifice plate flow measurement — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  4. D.Orifice plate flow measurement — differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
Reveal the answer + AI explanation — free account

4. What is Thermocouple?

Junior
  1. A.two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  2. B.differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  3. C.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  4. D.ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
Reveal the answer + AI explanation — free account

5. Which term means: "two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C"?

Junior
  1. A.Thermocouple
  2. B.Vortex flow meter
  3. C.HART protocol
  4. D.Coriolis mass flow meter
Reveal the answer + AI explanation — free account

6. Which statement is correct?

Junior
  1. A.Thermocouple — differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  2. B.Thermocouple — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  3. C.Thermocouple — platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  4. D.Thermocouple — digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
Reveal the answer + AI explanation — free account

7. What is Pt100 RTD?

Junior
  1. A.platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  2. B.two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  3. C.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  4. D.digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
Reveal the answer + AI explanation — free account

8. Which term means: "platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C"?

Junior
  1. A.Pt100 RTD
  2. B.HART protocol
  3. C.Coriolis mass flow meter
  4. D.DP level measurement
Reveal the answer + AI explanation — free account

9. Which statement is correct?

Junior
  1. A.Pt100 RTD — platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  2. B.Pt100 RTD — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  3. C.Pt100 RTD — ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  4. D.Pt100 RTD — bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number
Reveal the answer + AI explanation — free account

10. What is 4–20 mA signal?

Junior
  1. A.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  2. B.standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  3. C.differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  4. D.hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
Reveal the answer + AI explanation — free account

11. Which term means: "standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero"?

Junior
  1. A.Coriolis mass flow meter
  2. B.DP level measurement
  3. C.HART protocol
  4. D.4–20 mA signal
Reveal the answer + AI explanation — free account

12. Which statement is correct?

Junior
  1. A.4–20 mA signal — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  2. B.4–20 mA signal — standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  3. C.4–20 mA signal — ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  4. D.4–20 mA signal — vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
Reveal the answer + AI explanation — free account

13. What is DP level measurement?

Mid
  1. A.standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  2. B.hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
  3. C.bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number
  4. D.digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
Reveal the answer + AI explanation — free account

14. Which term means: "hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression"?

Mid
  1. A.Coriolis mass flow meter
  2. B.Thermocouple
  3. C.Orifice plate flow measurement
  4. D.DP level measurement
Reveal the answer + AI explanation — free account

15. Which statement is correct?

Mid
  1. A.DP level measurement — platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  2. B.DP level measurement — differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  3. C.DP level measurement — hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
  4. D.DP level measurement — bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number
Reveal the answer + AI explanation — free account

16. What is Coriolis mass flow meter?

Mid
  1. A.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  2. B.standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  3. C.digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
  4. D.ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
Reveal the answer + AI explanation — free account

17. Which term means: "vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run"?

Mid
  1. A.Coriolis mass flow meter
  2. B.DP level measurement
  3. C.Thermocouple
  4. D.Turndown ratio
Reveal the answer + AI explanation — free account

18. Which statement is correct?

Mid
  1. A.Coriolis mass flow meter — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
  2. B.Coriolis mass flow meter — hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
  3. C.Coriolis mass flow meter — ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  4. D.Coriolis mass flow meter — vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
Reveal the answer + AI explanation — free account

19. What is HART protocol?

Mid
  1. A.platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  2. B.digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
  3. C.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  4. D.standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
Reveal the answer + AI explanation — free account

20. Which term means: "digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring"?

Mid
  1. A.Coriolis mass flow meter
  2. B.Vortex flow meter
  3. C.Orifice plate flow measurement
  4. D.HART protocol
Reveal the answer + AI explanation — free account

21. Which statement is correct?

Mid
  1. A.HART protocol — standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  2. B.HART protocol — differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
  3. C.HART protocol — platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  4. D.HART protocol — digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
Reveal the answer + AI explanation — free account

22. What is Turndown ratio?

Senior
  1. A.ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  2. B.standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  3. C.digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
  4. D.platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
Reveal the answer + AI explanation — free account

23. Which term means: "ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis"?

Senior
  1. A.4–20 mA signal
  2. B.Turndown ratio
  3. C.HART protocol
  4. D.Orifice plate flow measurement
Reveal the answer + AI explanation — free account

24. Which statement is correct?

Senior
  1. A.Turndown ratio — ratio of maximum to minimum flow a meter reads within stated accuracy, about 4:1 for orifice plates against 20:1 or more for Coriolis
  2. B.Turndown ratio — digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
  3. C.Turndown ratio — standard analogue transmitter output where 4 mA is zero of range; the live zero lets a broken wire (0 mA) be distinguished from a true zero
  4. D.Turndown ratio — vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
Reveal the answer + AI explanation — free account

25. What is Vortex flow meter?

Senior
  1. A.bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number
  2. B.platinum resistance element reading 100 Ω at 0 °C and about 0.385 Ω per °C, more accurate and linear than a thermocouple but limited to about 600 °C
  3. C.vibrating tube whose phase shift between inlet and outlet sensors is proportional to mass flow, also giving density and needing no straight run
  4. D.differential pressure across a sharp-edged restriction where flow is proportional to the square root of DP, so the transmitter needs square-root extraction
Reveal the answer + AI explanation — free account

26. Which term means: "bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number"?

Senior
  1. A.4–20 mA signal
  2. B.DP level measurement
  3. C.HART protocol
  4. D.Vortex flow meter
Reveal the answer + AI explanation — free account

27. Which statement is correct?

Senior
  1. A.Vortex flow meter — hydrostatic head between bottom and top taps gives liquid level; a wet leg on the low side requires zero elevation or suppression
  2. B.Vortex flow meter — bluff body sheds vortices at a frequency proportional to velocity, well suited to steam and gas, but reads zero below a minimum Reynolds number
  3. C.Vortex flow meter — digital signal superimposed on the 4–20 mA loop so a handheld or DCS can read diagnostics and re-range the transmitter without rewiring
  4. D.Vortex flow meter — two dissimilar-metal junctions generating a Seebeck voltage proportional to temperature difference; K type (chromel-alumel) covers up to about 1200 °C
Reveal the answer + AI explanation — free account